For NCEES sample exam problem #524 the problem gives the % of Nameplate kVA and Total Losses as follows:
% of Nameplate kVA, Total Losses (W)
0 , 460
50 , 2,370.
It asks "The total transformer losses (W) at 100% of nameplate kVA is most nearly:
(B) 8,100 MW
The problem solves this by subtrcting no load losses from 2,370 to get 1,910 MW. It then multiples this number by 4 to get 7,640. It re-adds in the no load losses to get 8,100MW - answer B.
My question is why is multiply by 4 and not by 2. What is the convention that leads to multiply by 4. And does anybody know of a good refecence to read up on this.
Thanks!