For a single-line-to-ground fault (also called a single-phase-to-ground fault), the overall sequence network diagram has the positive (Z1), negative (Z2), and zero (Z0) sequence impedances all in series. So here:Hi, I also can't understand this problem.
I don't understand why Ia1 = 1.0/(2*Z1+Z0). Can anyone explain why?
A phase-to-ground fault occurs on the 33-kV transmission system shown in the figure...
View attachment 21907
Nonsymmetrical faults such as unbalanced three-phase faults, single line to ground faults, double line to ground faults, and line to line faults all have different fault circuit compared to each other that are a different combination of the positive, negative, and zero sequence network. These fault circuits can be found in the CBT Reference Handbook.Hi, I also can't understand this problem.
I don't understand why Ia1 = 1.0/(2*Z1+Z0). Can anyone explain why?
A phase-to-ground fault occurs on the 33-kV transmission system shown in the figure...
View attachment 21907