Hi Everybody,
I'm having an issue with this problem and it's driving me kind of nuts. I know I'm so close to the solution it's killing me but I just can't connect the dots. If anybody can help I'd greatly appreciate it!
A 1,000-kVA, 12.47-kV-480Y/277-V transformer with 4% impedance feeds a 480-V bus. The fault duty of the 12.47 kV system is 40 MVA. Assuming the transformer and the 12.47-kV system have the same X/R ration, the 3-phase short-circuit current (amperes) available at the 480-V bus is most nearly:
The solution is shown as Isc = 1.0 / 0.04 + 0.025 = 15.4 pu on a 1 MVA base. It looks like the numerator is the MVA base, and the denominator of this fraction is the combined per unit Z of the transformer and system, I get the 4% (0.04) impedance is in series with the system impedance, but I don't get how we get the 0.025 value. From there on I get it, finding the I base using the Base MVA / sqrt*3*480 = 1203 A and then Isc = 15.4 * 1203 = 18,526 A. That makes sense.
But..
0.025 is 1/40, but there's something I'm missing here. Is the impedance of the fault duty of a system is simply the inverse of the fault duty MVA rating? I can't find the term "fault duty" in any of the references I have. Since we know that the MVA of the system is 40 MVA, and the KV of the system is 12.47, then I first tried to find the current using those two (MVA / KV) and then find the Z using the result of that (KV / A) but that doesn't work here. I think the key is the 40 MVA fault duty but I can't figure out how it works. Please help! Thanks
I'm having an issue with this problem and it's driving me kind of nuts. I know I'm so close to the solution it's killing me but I just can't connect the dots. If anybody can help I'd greatly appreciate it!
A 1,000-kVA, 12.47-kV-480Y/277-V transformer with 4% impedance feeds a 480-V bus. The fault duty of the 12.47 kV system is 40 MVA. Assuming the transformer and the 12.47-kV system have the same X/R ration, the 3-phase short-circuit current (amperes) available at the 480-V bus is most nearly:
The solution is shown as Isc = 1.0 / 0.04 + 0.025 = 15.4 pu on a 1 MVA base. It looks like the numerator is the MVA base, and the denominator of this fraction is the combined per unit Z of the transformer and system, I get the 4% (0.04) impedance is in series with the system impedance, but I don't get how we get the 0.025 value. From there on I get it, finding the I base using the Base MVA / sqrt*3*480 = 1203 A and then Isc = 15.4 * 1203 = 18,526 A. That makes sense.
But..
0.025 is 1/40, but there's something I'm missing here. Is the impedance of the fault duty of a system is simply the inverse of the fault duty MVA rating? I can't find the term "fault duty" in any of the references I have. Since we know that the MVA of the system is 40 MVA, and the KV of the system is 12.47, then I first tried to find the current using those two (MVA / KV) and then find the Z using the result of that (KV / A) but that doesn't work here. I think the key is the 40 MVA fault duty but I can't figure out how it works. Please help! Thanks