NCEES Problem #70

Help Support Engineer Boards:

lost4ever

Member
Joined
May 11, 2018
Messages
22
Reaction score
0
Hi to all,
Can anyone help me with the impedance calculation.
base kva = 1000
base kV = 0.48
I got X p.u for transformer is 0.04
and for system is 0.67
I don't know what I am doing wrong?
 

Attachments

  • ncees 70.jpg
    ncees 70.jpg
    33.6 KB · Views: 71
  • ncees 70-answer.jpg
    ncees 70-answer.jpg
    31.3 KB · Views: 70

akyip

Member
Joined
Feb 7, 2020
Messages
334
Reaction score
106
Since the system and transformer have different KVA ratings, did you use the Zpu new = Zpu old * (Sbase new / Sbase old) * (Vbase old /Vbase new)^2 formula to convert one of the base impedances to the correct impedance value per the new system base?
 

lost4ever

Member
Joined
May 11, 2018
Messages
22
Reaction score
0
Yes I used the similar formula
Transformer : 0.04 (1000/1000)*(0.48/0.48)^2 = 0.04 p.u
System: 0.04 (1000/40000)(12.47/0.48)^2 = 0.67 p.u
 

RedRaider2020

Active member
Joined
Nov 30, 2020
Messages
26
Reaction score
6
Your KV pu is not correct.

12.47 System - Vbase=12.47 V=1 pu, MVAbase=1MVA MVA= 40 pu Z= (1)^2/40=.025 pu
12.47 side Transformer = Vbase= 12.47V V=1pu, MVAbase=1MVA MVA=1pu, Z= .04pu
480 side Transformer = Vbase=480V V=1pu, MVAbase=1MVA MVA = 1pu, Z= .04pu

I=V/Z Z=Ztransformer + Z system = .04pu + .025pu V=1pu V/Z=1/(.04+.025)=15.4
 
Last edited:

RedRaider2020

Active member
Joined
Nov 30, 2020
Messages
26
Reaction score
6
It's given in the problem "transformer with 4% impedence"
For transformers the PU impendence quantity is always given for the rated voltage and MVA.
If you're operating the transformer at a different voltage then you have to change the impendence but if you're operating it at the rated voltage and MVA and you've chosen those rated values as your base then you can just use the given PU impendence.
 
Last edited:

RedRaider2020

Active member
Joined
Nov 30, 2020
Messages
26
Reaction score
6
Voltage is the same as the base so it is 1. The MVA of the system =40MVA/The base MVA = 1 so 40/1 = 40pu. Z=V^2/S so 1^2/40=.025 pu
 

giginubs

Member
Joined
Jan 26, 2021
Messages
6
Reaction score
0
Voltage is the same as the base so it is 1. The MVA of the system =40MVA/The base MVA = 1 so 40/1 = 40pu. Z=V^2/S so 1^2/40=.025 pu
I'm assuming we are using the 1 MVA as a base since the Transformer Base is 1000KVA=1 MVA. You did this to make the math easier if I understand that correctly.

Also for the 40 MVA, is that considered the actual MVA value because I know that S_pu = S_actual/S_base so in that case would S_actual = 40 MVA and S_base=1MVA therefore S_pu is 40pu as you stated?
 

RedRaider2020

Active member
Joined
Nov 30, 2020
Messages
26
Reaction score
6
I'm assuming we are using the 1 MVA as a base since the Transformer Base is 1000KVA=1 MVA. You did this to make the math easier if I understand that correctly.

Also for the 40 MVA, is that considered the actual MVA value because I know that S_pu = S_actual/S_base so in that case would S_actual = 40 MVA and S_base=1MVA therefore S_pu is 40pu as you stated?
That's correct. You have to pick one base for the whole system so if you can pick one where all the values are 1 the math will be a lot easier. Yes 40MVA is the actual and divided by 1 becomes 40 pu. The values with units like MVA, KVA, KW, V, A will always be the actual value and the base is whatever base you choose it to be if they don't tell you to use a specific one in the question.
 

giginubs

Member
Joined
Jan 26, 2021
Messages
6
Reaction score
0
That's correct. You have to pick one base for the whole system so if you can pick one where all the values are 1 the math will be a lot easier. Yes 40MVA is the actual and divided by 1 becomes 40 pu. The values with units like MVA, KVA, KW, V, A will always be the actual value and the base is whatever base you choose it to be if they don't tell you to use a specific one in the question.
Thank you for the clarification!
 