Problem states impedance = 0.050+j0.050 ohms, 3 phase, and with a fixed 50A current. Question is to determine differences in voltage drop with unity pf, zero pf, and 0.707 lagging pf.
Solution uses NEC Chapter 9, table 9, V = I(XsinΦ + RcosΦ), and since X=R, voltage drop proportional to (sinΦ+cosΦ) only.
At 0.707 power factor, (sinΦ+cosΦ) = 1.414
Unity, (sinΦ+cosΦ) = 1.0
Zero pf, (sinΦ+cosΦ) = 1.0
Answer is at 0.707 pf... D
However, if you don't use NEC equation and work it out (solving for voltage drop), the answer is different!
At 0.707, V= |IZ| = (50<-45)*(0.05+j0.05) = 3.53V
At unity, V= |IZ| = (50<0)*(0.05+j0.05) = 3.53V
At zero pf, V= |IZ| = (50<90)*(0.05+j0.05) = 3.53V
I found that the power factor does not affect the voltage drop of the feeder (which according to NCEES, is wrong)
Can someone explain why calculating the voltage drop gives a different answer than using the NEC???
Solution uses NEC Chapter 9, table 9, V = I(XsinΦ + RcosΦ), and since X=R, voltage drop proportional to (sinΦ+cosΦ) only.
At 0.707 power factor, (sinΦ+cosΦ) = 1.414
Unity, (sinΦ+cosΦ) = 1.0
Zero pf, (sinΦ+cosΦ) = 1.0
Answer is at 0.707 pf... D
However, if you don't use NEC equation and work it out (solving for voltage drop), the answer is different!
At 0.707, V= |IZ| = (50<-45)*(0.05+j0.05) = 3.53V
At unity, V= |IZ| = (50<0)*(0.05+j0.05) = 3.53V
At zero pf, V= |IZ| = (50<90)*(0.05+j0.05) = 3.53V
I found that the power factor does not affect the voltage drop of the feeder (which according to NCEES, is wrong)
Can someone explain why calculating the voltage drop gives a different answer than using the NEC???