Just when I thought I had this nailed...kick in the nuts...
One of the items on my list of things to know cold for the exam, without any question, is when to use the nameplate current rating, and when to use table 430.250 or similar for motors.
I cannot find a clear answer on engineerboards...or at least not one that has me convinced....but after going over Art 430.6(A)(1) and (2) with a fine tooth comb, I've come to the following conclusion:
HOWEVER,
I am still confused by Art 430.6(A)(2) which says: Nameplate Values. Separate motor overload protection shall be based on the motor nameplate current rating. The handbook goes on to explain that the tables should be used for sizing conductors, branch circuit and ground fault protection, and ampere rating of motor disconnecting means RATHER than using the nameplate current.
So if I am understanding this all, if it's a motor overLOAD device you are sizing, you use the nameplate current regardless. If you are sizing conductors or OCPD for a regular motor, you use the tables regardless. IF AND ONLY IF you are sizing conductors or OCPD for a "motor-operated appliance," AND you are given nameplate current, you use the nameplate current and not the tables.
Please, someone clear this up for me...unless of course, there is no right answer and the next edition will be completely different...
Am I studying for the PE exam or to join the NEC committee?
One of the items on my list of things to know cold for the exam, without any question, is when to use the nameplate current rating, and when to use table 430.250 or similar for motors.
I cannot find a clear answer on engineerboards...or at least not one that has me convinced....but after going over Art 430.6(A)(1) and (2) with a fine tooth comb, I've come to the following conclusion:
- Unless the question clearly states a "motor-operated appliance", AND lists the nameplate current and HP, Art 430.6(A)(1) Exception 3 DOES NOT APPLY.
HOWEVER,
I am still confused by Art 430.6(A)(2) which says: Nameplate Values. Separate motor overload protection shall be based on the motor nameplate current rating. The handbook goes on to explain that the tables should be used for sizing conductors, branch circuit and ground fault protection, and ampere rating of motor disconnecting means RATHER than using the nameplate current.
So if I am understanding this all, if it's a motor overLOAD device you are sizing, you use the nameplate current regardless. If you are sizing conductors or OCPD for a regular motor, you use the tables regardless. IF AND ONLY IF you are sizing conductors or OCPD for a "motor-operated appliance," AND you are given nameplate current, you use the nameplate current and not the tables.
Please, someone clear this up for me...unless of course, there is no right answer and the next edition will be completely different...
Am I studying for the PE exam or to join the NEC committee?