Ref: AISC Seismic Design Manual 3rd Print
Seismic Provision 14.2 on page 6.1-48 States:
"Bracing Members in K, V, or inverted -V configurations shall have KL/r <= 4 (square root)(E/Fy)
For HSS memberswith Fy of 46ksi and E of 29,000 ksi, this is about 100. This greatly increase the size of the HSS bracing .
My question for you fellow structural engineers are:
1. If the wind load governs your lateral design at this braced frame, Does the brace still need to comply with this "Seismic Provision"? In other words, does this provision only apply when your Seismic Load governs the lateral design?
Typically I would design the brace just like a column member with KL/r <=200 when wind load governs
2. This seismic provision excludes diagonal "D" bracing - so does that mean the bracing can use KL/r if it is a diagonal braced frame?
Thanks in advance,
Seismic Provision 14.2 on page 6.1-48 States:
"Bracing Members in K, V, or inverted -V configurations shall have KL/r <= 4 (square root)(E/Fy)
For HSS memberswith Fy of 46ksi and E of 29,000 ksi, this is about 100. This greatly increase the size of the HSS bracing .
My question for you fellow structural engineers are:
1. If the wind load governs your lateral design at this braced frame, Does the brace still need to comply with this "Seismic Provision"? In other words, does this provision only apply when your Seismic Load governs the lateral design?
Typically I would design the brace just like a column member with KL/r <=200 when wind load governs
2. This seismic provision excludes diagonal "D" bracing - so does that mean the bracing can use KL/r if it is a diagonal braced frame?
Thanks in advance,