Eng. Pro Final Exam Problem 12

Professional Engineer & PE Exam Forum

Help Support Professional Engineer & PE Exam Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

no_concentrate

Active member
Joined
Mar 26, 2021
Messages
35
Reaction score
15
Eng. Pro Final Exam Problem 12 :
As per my knowledge primary is connected in Delta and secondary is connected in Star. During single line to ground fault on one phase of star connection other two phase i.e b and c will be zero. Since primary and secondary is linked so there will be no flow of current in C (primary ) also. I am confused about for why current will be zero in a phase of secondary.
 

Attachments

  • Eng pro final exam.png
    Eng pro final exam.png
    73.7 KB
Since this is a delta-wye xfmr, so phase A on the secondary side is paired with AB on the primary delta- hence current will be on both A and B on the primary side. A phase of the secondary doesn't have a source of current downstream.
 