First time working on this type of calc, just looking for input from someone who is used to doing heat load calcs
The cooling requirement seems incredible high to me. Is this right? ~45ton of cooling needed? This is for a <5000sqft building used as a nightclub with occupant load of 290.
I've going through the building code and meticulously reviewing all my input. Just seems really high to me, but i am not sure if this is typical of a nightclub
Walls
Loss
10169
Sensible Gain
3962
Latent Gain
0
Windows
1310
1505
0
Doors
5479
5822
0
Ceiling
3556
2540
0
Skylights
0
0
0
Floors
0
0
0
Room Internal Loads
0
84537
95485
Blower Load
1707
0
Hot Water Piping Load
0
0
Winter Humidification Load
0
0
0
Infiltration
0
0
0
Ventilation
176792
94710
249805
Supply Duct EHLF=0 ESGF=0
0
0
n/a
Return Duct EHLF=0 ESGF=0
0
0
0
Subtotal
197306
194783
345290
Total Heating
197306 Btuh
Total Cooling
540073 Btuh
The cooling requirement seems incredible high to me. Is this right? ~45ton of cooling needed? This is for a <5000sqft building used as a nightclub with occupant load of 290.
I've going through the building code and meticulously reviewing all my input. Just seems really high to me, but i am not sure if this is typical of a nightclub
Walls
Loss
10169
Sensible Gain
3962
Latent Gain
0
Windows
1310
1505
0
Doors
5479
5822
0
Ceiling
3556
2540
0
Skylights
0
0
0
Floors
0
0
0
Room Internal Loads
0
84537
95485
Blower Load
1707
0
Hot Water Piping Load
0
0
Winter Humidification Load
0
0
0
Infiltration
0
0
0
Ventilation
176792
94710
249805
Supply Duct EHLF=0 ESGF=0
0
0
n/a
Return Duct EHLF=0 ESGF=0
0
0
0
Subtotal
197306
194783
345290
Total Heating
197306 Btuh
Total Cooling
540073 Btuh