A distance relay is located at Bus A that looks outwards toward Bus C as shown in the diagram below.
Zone 1 of the distance relay covers transmission line AB and Zone 2 covers just beyond Bus C.
A fault occurs on Bus C. When Generator B is online and breaker 52 is closed, which of the following statements is true?
a) Generator B connected to the system has no effect on how the impedance relay sees a fault at Bus C.
b) With Generator B connected, the impedance seen by the relay appears to be greater.
c) The more current Generator B provides to Bus B, the more likely the relay will trip due to Zone 1.
d) None of the above.