Question is a 3 phase delta-wye 30MVA, 33kv/11kV transformer is protected by a differential relay
Calculate the relay current setting for faults up to 200 percent of the rated current. the CT current ratio is 500/5 for primary and 2000/5 on secondary.
The solution is attached. I understand everything except why the WYE CT current is multiplied by 1.73.
It could be the question is poorly written, but to me i read it as a single 3phase transformer and the CTs are measuring line currents. So to me the 1.73 multiplier is not necessary.
Calculate the relay current setting for faults up to 200 percent of the rated current. the CT current ratio is 500/5 for primary and 2000/5 on secondary.
The solution is attached. I understand everything except why the WYE CT current is multiplied by 1.73.
It could be the question is poorly written, but to me i read it as a single 3phase transformer and the CTs are measuring line currents. So to me the 1.73 multiplier is not necessary.