Hi there, Hope you, smart engineers, do not get tired of my quetions. I am planning to pass the exam this time and I do not want to leave any doubt behind me. I am hoping that my quetions not only will help me to understand the material better, It also help the others by discussing the questions here.
Here is my new dilemma,
A three phase, delta, wye connected, 30 MVA, 33/ 11 KV transformer is protected by a differential relay. Calculate the relay current setting for faults drawing up to 200 percent of the rated current. The CT current ratio on the primary side is 500:5, and that on the secondary side is 2000:5.
The primary line current is: Ip = (30 MVA)/ (1.73 X 33 KV) = 525 A
The secondary line current is: Is = 3 Ip = 3 X 525 = 1574.6 A
The CT current on the primary is: I1 = 525 / (500/5) = 5.25 A
CT on the secondary side is: I2 = 1574.5 X (5 / 2000) X (1.73)
why do we multiply by 1.73? It can't be base on the type of the connection since the right side of transformer is Y connection which means the I phase and I line are equal and we consider the primary side as 3 phase not single phase.
Thank you
Here is my new dilemma,
A three phase, delta, wye connected, 30 MVA, 33/ 11 KV transformer is protected by a differential relay. Calculate the relay current setting for faults drawing up to 200 percent of the rated current. The CT current ratio on the primary side is 500:5, and that on the secondary side is 2000:5.
The primary line current is: Ip = (30 MVA)/ (1.73 X 33 KV) = 525 A
The secondary line current is: Is = 3 Ip = 3 X 525 = 1574.6 A
The CT current on the primary is: I1 = 525 / (500/5) = 5.25 A
CT on the secondary side is: I2 = 1574.5 X (5 / 2000) X (1.73)
why do we multiply by 1.73? It can't be base on the type of the connection since the right side of transformer is Y connection which means the I phase and I line are equal and we consider the primary side as 3 phase not single phase.
Thank you