Hey guys,
I have a question specifically about using the 90-degree C ampacity from the conductor ampacity tables in NEC Article 310. This comes from Eng. Pro Guides Full Exam Problem 78, which asks for the 90-degree C ampacity required for a combination motor and continuous non-motor load.
Here, the required conductor ampacity is 45 A (1.25 x 26 A + 1.25 x 10 A). Then, in the solution for Problem 78, it simply uses Table 310.15(B)(16) to find the required copper size at 90 degree C.
My question is: doesn't NEC Article 100.14(C)(1)(a) prevent you from using the 90-degree ampacity in this situation? This article reads:
"Termination provisions of equipment for circuits rated 100 amperes or less, or marked for #14 AWG through #1 AWG conductors, shall be used only for one of the following:
(1) Conductors rated 60 degrees C (140 degrees F)
(2) Conductors with higher temperature ratings, provided the ampacity of such conductors is determined based on the 60 degrees C (140 degrees F) ampacity of the conductor size used
(3) Conductors with higher temperature ratings if the equipment is listed and identified for use with such conductors
(4) For motors marked with design letters B, C, or D, conductors having an insulation rating of 75 degrees C (167 degrees F) or higher shall be permitted to be used, provided the ampacity of such conductors does not exceed the 75 degrees C (167 degrees F) ampacity"
This is something I learned from another practice exam, from Zach Stone's Electrical PE Review. His exam has a similar NEC problem where the circuit's rated current exceeds 100 A, and per NEC 110.14(C)(1)(b), for circuits over 100 A you can only use the 75-degree C ampacity at most to size conductors for circuits rated over 100 A. I'm trying to see if a similar logic with NEC 110.14(C)(1)(a) for circuits rated 100 A or less holds for this problem.
NEC 110.14(C)(1) also makes me think and question - when can you actually use the 90-degree C ampacity column for properly sizing conductors?
Let me know what you guys think... thank you!
I have a question specifically about using the 90-degree C ampacity from the conductor ampacity tables in NEC Article 310. This comes from Eng. Pro Guides Full Exam Problem 78, which asks for the 90-degree C ampacity required for a combination motor and continuous non-motor load.
Here, the required conductor ampacity is 45 A (1.25 x 26 A + 1.25 x 10 A). Then, in the solution for Problem 78, it simply uses Table 310.15(B)(16) to find the required copper size at 90 degree C.
My question is: doesn't NEC Article 100.14(C)(1)(a) prevent you from using the 90-degree ampacity in this situation? This article reads:
"Termination provisions of equipment for circuits rated 100 amperes or less, or marked for #14 AWG through #1 AWG conductors, shall be used only for one of the following:
(1) Conductors rated 60 degrees C (140 degrees F)
(2) Conductors with higher temperature ratings, provided the ampacity of such conductors is determined based on the 60 degrees C (140 degrees F) ampacity of the conductor size used
(3) Conductors with higher temperature ratings if the equipment is listed and identified for use with such conductors
(4) For motors marked with design letters B, C, or D, conductors having an insulation rating of 75 degrees C (167 degrees F) or higher shall be permitted to be used, provided the ampacity of such conductors does not exceed the 75 degrees C (167 degrees F) ampacity"
This is something I learned from another practice exam, from Zach Stone's Electrical PE Review. His exam has a similar NEC problem where the circuit's rated current exceeds 100 A, and per NEC 110.14(C)(1)(b), for circuits over 100 A you can only use the 75-degree C ampacity at most to size conductors for circuits rated over 100 A. I'm trying to see if a similar logic with NEC 110.14(C)(1)(a) for circuits rated 100 A or less holds for this problem.
NEC 110.14(C)(1) also makes me think and question - when can you actually use the 90-degree C ampacity column for properly sizing conductors?
Let me know what you guys think... thank you!