If you have a nameplate full load current of a motor, when do you use the nameplate value vs looking up from hp in table 430.250 to calculate ampacity for choosing the proper conductor size?
The solution for proguide 78 test says use the table to get 26 amps, but I thought since 30 amps was given, to take 125% of that?
The solution for proguide 78 test says use the table to get 26 amps, but I thought since 30 amps was given, to take 125% of that?