So the question states:
A 34.5kv, 3-phase, 4-wire, wye-connected distribution planel is experiencing an unbalanced load situation. On phase A (19.9<0) there is a 120+j65 kva load, on phase C (19.9<0) there is a 65+j20 kva load. Calculate the magnitude of the neutral current.
Ok, so I get the fact that V phase A = 19.9<0 and V phase C = 19.9<240 (assuming ABC sequence) and that Ineutral will equal the sum of the current in phase A and C or Ia+Ic-In=0.
Why is the solution then the impedance of the load divided by the voltage equals the current?? Thought V=I * Z. CI in the solution also shows the currents to be the conejugate of the current? Why is this?
Thanks in advance for your help.
A 34.5kv, 3-phase, 4-wire, wye-connected distribution planel is experiencing an unbalanced load situation. On phase A (19.9<0) there is a 120+j65 kva load, on phase C (19.9<0) there is a 65+j20 kva load. Calculate the magnitude of the neutral current.
Ok, so I get the fact that V phase A = 19.9<0 and V phase C = 19.9<240 (assuming ABC sequence) and that Ineutral will equal the sum of the current in phase A and C or Ia+Ic-In=0.
Why is the solution then the impedance of the load divided by the voltage equals the current?? Thought V=I * Z. CI in the solution also shows the currents to be the conejugate of the current? Why is this?
Thanks in advance for your help.