This is a PF correction problem which I thought I could do in my sleep until I got this one wrong. I calculated that this delta-connected 460V motor, 96A phase current, at a 0.70 lagging pf has S=132kVA <45.6. A capacitor then corrects this to a 0.95 lagging pf and it asks for the real power produced by the motor (I assume they mean consumed).
The solution states that you can simply take 132kVA x 0.95 = 126kW. But isn't P unchanged regardless of PF here, at 132kVA (cos 45.6) = 92kW?
The solution states that you can simply take 132kVA x 0.95 = 126kW. But isn't P unchanged regardless of PF here, at 132kVA (cos 45.6) = 92kW?