3 Phase Load Question

Professional Engineer & PE Exam Forum

Help Support Professional Engineer & PE Exam Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

knight1fox3

Jedi MASTER & Friend of Capt. Solo
Joined
Dec 30, 2009
Messages
16,366
Reaction score
4,067
Location
Brew City!
In the attached PDF, if I have 3 resistors connected in a delta configuration to a 480V 3-phase source as shown, what will be the total current draw in each phase?

Circuit_Load.pdf

 

Attachments

  • Circuit_Load.pdf
    23.4 KB
I assume you're looking for the line current being supplied to the network:

ILine = sqrt(3)*IPhase = sqrt3*30 = 51.96 Amps

 
I assume you're looking for the line current being supplied to the network:
ILine = sqrt(3)*IPhase = sqrt3*30 = 51.96 Amps
You are correct. So 51.96A is being supplied in each phase.

I had a discussion with a colleague of mine who said that 60A was being drawn in each phase. I said I disagreed and wanted to confirm my understanding of this circuit. :)

 
In the attached PDF, if I have 3 resistors connected in a delta configuration to a 480V 3-phase source as shown, what will be the total current draw in each phase?
your schematic is correct, just make sure you are not confusing the line values with phase values. When you are converting a three phase circuit to a single phase like the way you did, the line and phase currents are equal in per phase schematic but when you convert it back to three phase you have to subtract the phase currents sharing the common line to find the target line current, and due to the 120 degree phase shift, line current magnitude turns out to be (3^.5) times phase current.

 
So is what I said in my 2nd post correct then?
Yes.

Another way to look at it is this: The currents are not scalar quantities, they are vectors. If you apply KCL to any of the three corners of the delta, the incoming line current will be equal to the sum of the two phase currents. In a balanced system, these phase currents will be separated by 120o.

Using your example of a 30 Amp phase current, you will get a line current = (30/0o)-(30/120o) = 51.96/-30o.

Edit: I would also suggest switching the direction of the arrow you show for current between phases A and C.

 
Last edited by a moderator:
Back