Hey guys,
In this Shorebrook Exam question 74 about two-wattmeter power factor, my initial attempt to solve for the power factor was using:
tan(theta) = sqrt(3) * (Phigh - Plow) / (Phigh + Plow) = 1.732 * (12 KW - 8.7 KW) / (12 KW + 8.7 KW) = 0.276
power factor angle: theta = tan^-1 (0.276) = 15.4295 degrees
power factor: p.f. = cos(15.4295 degrees) = 0.964
However, the given solution calculates pf = P/S, with:
P = P WA + P WB = 8.7 KW + 12 KW = 20.7 KW
S = sqrt(3) * V LL * I L = 1.732 * 300 V * 50 A = 25.98 KVA
P/S = 20.7 KW / 25.98 KVA = 0.8
What's the best explanation as to why these 2 power factor equations are yielding 2 different power factor answers for this problem?
Thanks for any input on this!
In this Shorebrook Exam question 74 about two-wattmeter power factor, my initial attempt to solve for the power factor was using:
tan(theta) = sqrt(3) * (Phigh - Plow) / (Phigh + Plow) = 1.732 * (12 KW - 8.7 KW) / (12 KW + 8.7 KW) = 0.276
power factor angle: theta = tan^-1 (0.276) = 15.4295 degrees
power factor: p.f. = cos(15.4295 degrees) = 0.964
However, the given solution calculates pf = P/S, with:
P = P WA + P WB = 8.7 KW + 12 KW = 20.7 KW
S = sqrt(3) * V LL * I L = 1.732 * 300 V * 50 A = 25.98 KVA
P/S = 20.7 KW / 25.98 KVA = 0.8
What's the best explanation as to why these 2 power factor equations are yielding 2 different power factor answers for this problem?
Thanks for any input on this!