question reads: "what is the current for a 3-phase, delta-connected, 200kVA load with a power factor of 0.92 if the supplied voltage is 12.5k V?

so I assumed the load is the total 3-phase load and the voltage is L-L. so the line current is I=200kva/sqrt(3)/12.5kV = 9.2A

solutions say that all you need to do is S=VI so I=200kVA/12.5kV = 16. this is only right if the load is per phase correct?

thanks

 
Rick I have the exact same issue with this question, and get the same answer as you, 9.2A = Iline. I believe ComplexImaginary is very wrong with their answer. The only other way to read this question is that they're asking for the current in the delta connected load (phase current). If so the answer would be 9.2 / sqrt(3) = 5.3, which is not an answer choice. The use of S = VI in the solution is simply not correct for this 3 phase problem.

 