Bare copper in PVC conduit so they won't SC, If you use insulated wire then you would have to use the effective ZActually with bare copper there will be 0 volts at the load because of short circuit. I am assuming that the distance to the load is 500' and not 250'.
I am getting 119 volts with insulated wires.
Yes uncoated copper,For single phase, you do need to include the impedance of the return path, because it affects the voltage at the load. For balanced 3-phase loads, the return path is the neutral, but no current flows through it, so its impedance is ignored.
You probably wanted to say uncoated copper and not bare.
Yes uncoated copper,For single phase, you do need to include the impedance of the return path, because it affects the voltage at the load. For balanced 3-phase loads, the return path is the neutral, but no current flows through it, so its impedance is ignored.
You probably wanted to say uncoated copper and not bare.
Got that from a CI problem. Don't remember which one.
What about the impedance if asked for the current draw from a single phase load? Is the impedance 2x even though it goes to the load and not back?