So, I have this 8000 gallon elevated horizontal tank that is supported on 2 concrete piers. The tank consists of 2 4ft diameter, ~50ft long vessels that are stacked on top of each other. I designed the piers and footings, but now I've been informed that we need to provide secondary containment for the tank. We need to be able to contain at least 50% of the tank volume so that the liquid does not pond under the tank. The other requirements are that the entire containment area must be able to contain 50% of the tank volume + 10 inches of rain OR 110% of the tank volume (higher volume controls).
My slab around the piers will be at grade. So, for the 50% without ponding, I laid out a 58'x10'x1'deep pit (580 cubic ft > 4000 gal --> 535 cubic feet). Then, for the 10" of rain, I said that the wall around the entire containment area has to be a minimum of 10" (we'll probably use 1') above grade. It seems to me that this is all I need to do... Am I missing something? It seems to easy.
Oh, I forgot to mention, the slab at grade will be sloped toward the pit, and the pit will be sloped toward a small sump pit in one corner where a portable pump can be placed as needed.
Thanks.
My slab around the piers will be at grade. So, for the 50% without ponding, I laid out a 58'x10'x1'deep pit (580 cubic ft > 4000 gal --> 535 cubic feet). Then, for the 10" of rain, I said that the wall around the entire containment area has to be a minimum of 10" (we'll probably use 1') above grade. It seems to me that this is all I need to do... Am I missing something? It seems to easy.
Oh, I forgot to mention, the slab at grade will be sloped toward the pit, and the pit will be sloped toward a small sump pit in one corner where a portable pump can be placed as needed.