problem # 513 ncees power

Professional Engineer & PE Exam Forum

Help Support Professional Engineer & PE Exam Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

ros

Member
Joined
Feb 5, 2011
Messages
23
Reaction score
0
hello,

prob 513..

i need help with this problem...

base (100mva and 12 kv)

i understand how they came up with Ibase. and then how they come up with 1 PU for Transformer... but i am having difficulty in calculating PU for 20 mile long transmission line...

given 0.145/1000ft... so for 20 miles... Z = J0.145*(20000/1000) = 2.9 ohms (IS THIS CORRECT)

SO NOW ZPU FOR TRANSMISSION LINE WILL BE = 2.9 / (Vbase/Ibase) = 2.9/2.49 pu...

can some one help me with this

 
hello,
prob 513..

i need help with this problem...

base (100mva and 12 kv)

i understand how they came up with Ibase. and then how they come up with 1 PU for Transformer... but i am having difficulty in calculating PU for 20 mile long transmission line...

given 0.145/1000ft... so for 20 miles... Z = J0.145*(20000/1000) = 2.9 ohms (IS THIS CORRECT)

SO NOW ZPU FOR TRANSMISSION LINE WILL BE = 2.9 / (Vbase/Ibase) = 2.9/2.49 pu...

can some one help me with this
1 Mile = 5280 ft

 
ok ... so Z for transmission line will be (0.145*20*5280) / 1000 = 15.312 ohm

now Zbase is 2.49 ....

so Z pu = 15.312/2.49 is this correct ?

if not .. help me solve this problem...

thanks

 
finally i am able to solve this problem.... but still i have confusion in finding short ckt current

i found that Z trans = 1 PU and Z trans line = 10.6 pu

but why SC = I base / ( 1 + 10.6) , where I base = 100mva/(sq 3 * 12 kv)

any help on that

thanks

 
finally i am able to solve this problem.... but still i have confusion in finding short ckt current
i found that Z trans = 1 PU and Z trans line = 10.6 pu

but why SC = I base / ( 1 + 10.6) , where I base = 100mva/(sq 3 * 12 kv)

any help on that

thanks
See Attached file

413.pdf

 

Attachments

  • 413.pdf
    16 KB · Views: 747
finally i am able to solve this problem.... but still i have confusion in finding short ckt current
i found that Z trans = 1 PU and Z trans line = 10.6 pu

but why SC = I base / ( 1 + 10.6) , where I base = 100mva/(sq 3 * 12 kv)

any help on that

thanks
See Attached file

thanks a lot ... but i am not able to understand the concept of Isc = Ib/Zpu

any help on that

thanks

 
finally i am able to solve this problem.... but still i have confusion in finding short ckt current
i found that Z trans = 1 PU and Z trans line = 10.6 pu

but why SC = I base / ( 1 + 10.6) , where I base = 100mva/(sq 3 * 12 kv)

any help on that

thanks
See Attached file

thanks a lot ... but i am not able to understand the concept of Isc = Ib/Zpu

any help on that

thanks
You are looking for the actual current at the fault. I actual = I base * I pu. = I base / Zpu. since Ipu = Vpu/Zpu note, Vpu=1

same way as S fault = S base / Zpu. I hope I didn't confuse you.

 
no u didnt confuse me.. u actually made my concept clear...thank you

 
I solved this using MVA Method as well

z_line=j0.145/1000ft * 5280ft/mi * 20 mi = 15.312 ohms

7.5MVA/.075 = 100MVA

(12kv)^2 / 15.312 ohms = 9.4 MVA

Both are in series

100*9.4 / (100+9.4) = 8.59 MVA

I_line = 8.59MVA / (sqrt(3) * 12kv)) = 413A

 
I solved this using MVA Method as well
z_line=j0.145/1000ft * 5280ft/mi * 20 mi = 15.312 ohms

7.5MVA/.075 = 100MVA

(12kv)^2 / 15.312 ohms = 9.4 MVA

Both are in series

100*9.4 / (100+9.4) = 8.59 MVA

I_line = 8.59MVA / (sqrt(3) * 12kv)) = 413A
Why are the MVAsc's calculated in parallel? And if following this logic, would parallel MVA's be calculated in as series MVAsc?

Please advice...I'm not very familiar with this method...it does look quicker.

Thanks!

 
I solved this using MVA Method as well
z_line=j0.145/1000ft * 5280ft/mi * 20 mi = 15.312 ohms

7.5MVA/.075 = 100MVA

(12kv)^2 / 15.312 ohms = 9.4 MVA

Both are in series

100*9.4 / (100+9.4) = 8.59 MVA

I_line = 8.59MVA / (sqrt(3) * 12kv)) = 413A
Why are the MVAsc's calculated in parallel? And if following this logic, would parallel MVA's be calculated in as series MVAsc?

Please advice...I'm not very familiar with this method...it does look quicker.

Thanks!
Yes, you actually add MVAsc as a capacitors.

 
I solved this using MVA Method as well
z_line=j0.145/1000ft * 5280ft/mi * 20 mi = 15.312 ohms

7.5MVA/.075 = 100MVA

(12kv)^2 / 15.312 ohms = 9.4 MVA

Both are in series

100*9.4 / (100+9.4) = 8.59 MVA

I_line = 8.59MVA / (sqrt(3) * 12kv)) = 413A
Why are the MVAsc's calculated in parallel? And if following this logic, would parallel MVA's be calculated in as series MVAsc?

Please advice...I'm not very familiar with this method...it does look quicker.

Thanks!
Yes, you actually add MVAsc as a capacitors.
take a look at this thread. It has the link to the MVA method papers.

http://engineerboards.com/index.php?showtopic=11332

 
Back
Top