I agree that the answer to this question is the AWG 4 conductor.
But since the circuit is at less than 100amps and according to NEC Section 110.14C1, shouldn't the left-most column for 60 deg C be used?
In this particular problem with the current 66.7A, the 60 and 75 deg C columns both say to use AWG 4.
But let's says the total current was was 71A, then doesn't 110.14C1 say that AWG 3 is the minimum size?
But since the circuit is at less than 100amps and according to NEC Section 110.14C1, shouldn't the left-most column for 60 deg C be used?
In this particular problem with the current 66.7A, the 60 and 75 deg C columns both say to use AWG 4.
But let's says the total current was was 71A, then doesn't 110.14C1 say that AWG 3 is the minimum size?