For this problem how is the percent z value calculated for the 40MVA system (Assuming the 1MVA Base)? The problem has .025 for the system impedance.

 
I am attempting to solve this problem by the MVA method where...

SC TX= 1MVA/4%= 25MVA

SC Sys= 40MVA/4%= 1000MVA

SC Tot= (In Parallel) so answer is about 24.4MVA

Ssc= 24.4MVA/ (sqrt3*480)= 29,348A. ?????

NCEES Answer 18,500.

 
Thanks Flyer PE!!! I get the PU Method now. In my error above they simplified the problem by directly giving us the SC of the system as 40MVA . Therefore the TX SC is (25MVA) and the system SC is (40MVA). It all works out now.

Couldn't find this problem using the search function.

 
Couldn't find this problem using the search function.
I also used to have troubles finding threads that already existed on NCEES problems using the EB.com search function. What I did to remedy this was to use G-o-o-g-l-e and type in for instance "NCEES 530" and the "engineerboards.com" after that and it would usually come up with a link to a thread on this site if one existed.

 
Thank you So much................this problem was bugging me about MVA method,  but this thread solved my problem. 

 