A room in a building has the following characteristics:
Sensible heat gain = 90,000 Btu/hr
Latent heat gain = 40,000 Btu/hr
Supply air to the room = 3,600 com @ 55ºF db
The room is kept at 78ºF db/ 45%rh. Outdoor air conditions are 92ºF db/ 76ºF wb. Outdoor air ventilation for the room is 700 com. The cooling coil entering-air temperature and leaving-air temperature, respectively are most nearly:
In the solution, the equation for the load is shown as QT = SH + LH + OA = 163,264 BTU/hr.
If SH= 90,000 BTU/hr and LH = 40,000 BTU/hr, then OA has to be 33,264 BTU/hr. I don't know how they calculated the OA load..... can someone help explain how they got that?