Anyone,
Seismic Design Manual, Vol 3. Page 293.
Why do they check Asmin for the negative moment on the section (bw = 24"), but not on the positive moment (bw = 52")?
ACI 21.3.2.1 says: At any section of a flexural member,
except as provided in 10.5.3, for top as well as for bottom
reinforcement, the amount of reinforcement shall
not be less than that given by Eq. (10-3) but not less
than 200bwd /fy, and the reinforcement ratio, ρ, shall
not exceed 0.025. At least two bars shall be provided
continuously both top and bottom.
Any thoughts? If they used the minimum steel, they would need 5.72 in2.