The question asks you to determine the appropriate size UF Al (60 degC) conductor using NEC for a 3HP continuous duty motor. I understand the load amperage is 25x1.25=31.3A. Using table 310.15, an 8AWG conductor can carry 35A, which is what I selected since its greater than FLAx25%.
However, the answer in the book selects 6AWG which is capable of 40A. Isn't the minimum size conductor the 8AWG?
Please help.
Thanks.