This is a simple problem with two 5kVA motors in parallel, one with PF=0.75 and the second with PF=0.65 both lagging. The question asks to find the total system power factor. The relevant answers are:
B ) 0.69
C) 0.71
The right way to do this problem is find the complex power for each and add them. 5 <41.41 + 5 <49.458= 9.97 <45.434. Cos 45.434 = 0.7017. Ideally I'd say the answer is neither B nor C but 0.7. But the book answer is C.
Common sense tells me it should be a straight average of the two PFs, so 0.7. Carrying 4 decimals through the calc I get the PF= 0.7017. I want to make sure I'm doing this right as I was certainly pulling hairs while taking this practice test. This test's answers are so close together that rounding can cause an incorrect answer. Does the PE play this game?
B ) 0.69
C) 0.71
The right way to do this problem is find the complex power for each and add them. 5 <41.41 + 5 <49.458= 9.97 <45.434. Cos 45.434 = 0.7017. Ideally I'd say the answer is neither B nor C but 0.7. But the book answer is C.
Common sense tells me it should be a straight average of the two PFs, so 0.7. Carrying 4 decimals through the calc I get the PF= 0.7017. I want to make sure I'm doing this right as I was certainly pulling hairs while taking this practice test. This test's answers are so close together that rounding can cause an incorrect answer. Does the PE play this game?