Complex Imaginary Exam 1 Prob 26- overcurrent protection

Professional Engineer & PE Exam Forum

Help Support Professional Engineer & PE Exam Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

ElecPwrPEOct11

Well-known member
Joined
Sep 22, 2011
Messages
116
Reaction score
0
Location
Virginia
For 300kcmil, TW, 60 degree cable the question asks what's the largest allowable overcurrent device:

A) 150A

B ) 180A

C) 200A

D) 225A

The allowable ampacity of the conductor is 190A from the NEC. However this is not a standard ampere rating per 240.6. NEC 240.4 (B ) allows you to round up to the next highest standard size 200A, except in a couple of very specific instances. Due to this, 200A is the correct answer. Can someone explain why the given solution of 180A is instead correct? Thanks.

 
I think you are right...200Amp shall be the over current protection. article 240.6(A) gives the standard breaker sizes and since the feeder is less than 800 amps you are allowed to use a higher breaker on a lower rating wire. For the people that don't know the wire specified in the problem is aluminum wire.

 
I also agree with your answer. I've submitted it as an errata but it has not been corrected yet.

 