I am using MVA method to calculate fault current and i got 8018 A but the CI solution is 8027 A. Could anyone please let me know if i am missing something :

Sg1 = 30 MVA/0.24 = 125 MVA,

SG2 = 20 MVA/0.24 = 83.33 MVA

Since the generators are in parallel, i added both MVAs = SG1+SG2 = 208.33 MVA

I fault = Stotal/(VLine * sqrt (3))

= 208.33 / (15*sqrt(3)) = 8018.7 Amperes

 
I am using MVA method to calculate fault current and i got 8018 A but the CI solution is 8027 A. Could anyone please let me know if i am missing something :

Sg1 = 30 MVA/0.24 = 125 MVA,

SG2 = 20 MVA/0.24 = 83.33 MVA

Since the generators are in parallel, i added both MVAs = SG1+SG2 = 208.33 MVA

I fault = Stotal/(VLine * sqrt (3))

= 208.33 / (15*sqrt(3)) = 8018.7 Amperes


You look good. It could easily be some rounding differences.

 
Some of the options to NCEES questions are very close so want to make sure there are no numerical errors. Thanks for the sanity check.

 