  1. E

    NCEES 530 (Calculate %Z)

    Thanks Flyer PE!!! I get the PU Method now. In my error above they simplified the problem by directly giving us the SC of the system as 40MVA . Therefore the TX SC is (25MVA) and the system SC is (40MVA). It all works out now. Couldn't find this problem using the search function.
  2. E

    NCEES 530 (Calculate %Z)

    I am attempting to solve this problem by the MVA method where... SC TX= 1MVA/4%= 25MVA SC Sys= 40MVA/4%= 1000MVA SC Tot= (In Parallel) so answer is about 24.4MVA Ssc= 24.4MVA/ (sqrt3*480)= 29,348A. ????? NCEES Answer 18,500.
  3. E

    NCEES 530 (Calculate %Z)

    For this problem how is the percent z value calculated for the 40MVA system (Assuming the 1MVA Base)? The problem has .025 for the system impedance.
  4. E

    Rules on what notes materials you can take in - printed, handwritten?

    Kenny did you take the exam in Illinois?
  5. E

    NEC Table for Nema Enclosures?

    Many thanks to both of you . The 2011 NEC does not have the Table 110.20.
  6. E

    NEC Table for Nema Enclosures?

    Does anyone know which table/page are the Nema Enclosure types found in the NEC? Or does it even exist within the NEC?
  7. E

    Short Circuit Question (NCEES vs Complex Imaginary Test 1-#

    Is the impedance of a TX correlated to the applied voltage for the short circuit? On Question 539 TX has 10% impedance & (100/7.2KV) and the factory short circuit test the applied KV to get rated current the answer is 10KV. (100KV * 10%) On complex imaginary TX has 5% impedance &amp...
  8. E

    Illinois PE Exam Materials Allowed in Test (HELP!)

    A friend of mines took the test in OCT 11 (Elec-Pwr) and he informed me that they proctors did not take any 3-Ring Binders from anyone as long as all the papers were bounded. They did take the NCEES practice booklet and Schaum's book from ppl though. Hope that helps. I plan to bring my binder...
  9. E

    Wanted PE-Power Complex Imaginary Tests

    I am looking to purchase the full-set (total of 4) of Complex Imaginary Prep Tests for the PE- Power Option. Please reply or send me a PM of what you have for sale. Thanks.
  10. E

    Spin-Up Sample Exam Problems Discussion

    Back to question 2-65 the question asks for load factor. My formula for this is LF=(Avg Load)/(Peak Load). But the answer provided is a formula for capacity factor. CF= (Avg Load for a period)/(Output Capacity of Plant). This is according to my reference book. Aren't these two things...
Back