stinkycheese

Capacitor Banks - calculating series/parallel kVAR

4 posts in this topic

There are a few questions from Complex Imaginary that ask about capacitor banks. To pick one (4-70), a 3P motor needs its PF improved by 3360 kVARs, using 140 kVAR units. The answer seems to be a straightforward 1120 kVAR/phase, or 8 units per phase. What I'm confused about is that CI claims that for three-phase banks, whether the units are in series or parallel, you just add the kVARs. Is this correct? AFAIK a capacitor's kVAR rating is for a spec'd supply voltage, and that kVAR rating varies with the square of voltage. So if you put 8 of those units in series, each unit will have its kVAR rating cut by a factor of 64-- and 8 140kVAR units become a 17.5 kVAR equivalent. Whereas 8 in parallel at rated voltage would give you the 1120kVAR/phase you're looking for. Is CI assuming that if you're putting 8 in series, you'd pick units rated for 140kVAR at Vline/8?

Thanks!

Share this post


Link to post
Share on other sites
 photo CHPE_AnimatedWebBanner_650x1202_zps5704d467.gif

I don't have this volume. Can you give a little more info about their solution? Is it 8 per phase? Do they give you the operating voltage and rated voltage?

Share this post


Link to post
Share on other sites

The question asks- for a three-phase motor requiring 3360kVAR in PF correction, you have 140 kVAR units. How many would you need per phase, if the units are to be connected in series?

CI's answer is for 8 per phase. They say in the solution that series/parallel combinations don't matter, you just add the total kVAR. No mention of the individual units' kVAR.

If you have the other books, 1-57, 2-17, and 3-72 are similar.

Share this post


Link to post
Share on other sites

I don't have a good answer. The only thing I can think of is that they're specifiying kVar vaules instead of farad values of the capacitors, so if you have 140kVar units connected in parallel, you get that kVar value at full voltage. If you connect 140kVar units in series, you get that kVar value at the divided voltage amongst the other units but either way, you get the same total kVar. The solution explantion may be misleading, because I don't see how the exact same units could be connected in series or parallel and still have the same total kVar value. Hopefully someone can confirm/explain better.

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!


Register a new account

Sign in

Already have an account? Sign in here.


Sign In Now
Sign in to follow this  
Followers 0