Xfmr ?

Professional Engineer & PE Exam Forum

Help Support Professional Engineer & PE Exam Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

Redskinsdb21

Well-known member
Joined
May 5, 2011
Messages
177
Reaction score
1
We have a 45 KVA, 3-phase, 480-120/208 V Xfmr, determine secondary conductors size annd secondary overcurrent device?

The solution says:I = VA divided by (208*1.732) = 45kva divided by (208*1.732) = 125 Amps, why do they multiply line to line voltage, by 1.732, shouldnt they divide by 1.732 other than multiply by it to get line to neutral voltage?

 
The solution is correct. If 120V is used you need to divide the total KVA by 3 since is a 3 phase this equal 15 kva per phase.

Now 15kva/120=125 amps

Which give the same answer.

I wish i can help you better understand this but the only way to learn this is going thru the college book and learn about 3-phase systems..let me know if you have a book that teach you this. If not i can recommend one that will help you a lot.

Now if my memory is correct thats the full load amps...so I suggest an over current protection of 150amps since you cant load a breaker more than 80%... thats takes care of breaker size...and the wire shall be 1/0. Now if fuses are used 125 amps is fine and the wire can be #2 per code is allowed, but in reality i suggest to go with #1. Im using copper with 75 d. insulation.

 