Voltage drop using new reference handbook for 3 phase NOT unity power factor

Professional Engineer & PE Exam Forum

Help Support Professional Engineer & PE Exam Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

Sparky Bill PE

Senior, Master, Professional, Licensed Electrical
Joined
Jun 30, 2019
Messages
303
Reaction score
149
Location
Chattanooga TN
I don't see how this formula can be line-to-neutral voltage drop, when it doesn't even consider the length of cable run. 

image.png

 
I don't see how this formula can be line-to-neutral voltage drop, when it doesn't even consider the length of cable run. 

View attachment 19462
I recognize this formula from NEC Chapter 9 Table 9. This is from one of the small notes just under the end of Table 9. In the NEC, this formula uses the ohms per unit length values for R and X.

But here, the NCEES reference handbook calls R and X as ohmic values instead of ohms per unit length values... Don't know why they did that...

 