That was Ives Substation in South Florida. The fault was inside the transformer. The F-Switch at the high side had a burnt trip coil and did not operate. As a result it kept feeding the fault inside the transformer.
Yep. I had the privilege of working for an engineer that was involved in the investigation. I even had the video in my flash card without knowing all the details. I showed it to him once and he told me: "That was Ives Sub and it happened because....." and gave me the whole explanation.+2 JR! very cool...and that happened all because of a bad trip coil.
That is just a local denomination to the disconective switches the company I used to work had. The SF6 breakers were the top of the line, then the F-Switch( Usually with SF6 bottles to take care of the arc and MOD), G-Swilth and L-Switch(these ones for distirbution). I am sure you have those on your system too but know name them differently.Say Bio, just curious, what's an F-switch? That's not in my lexicon but I bet I know it by a different name.