There is a problem in the PPI Six Minute Solutions for HVAC/Refrigeration that requires you to calculate whether or not a reheat coil should be added to classroom HVAC unit. The unit supplies 1000 CFM of supply air to the room. The classroom contains kids, age 7.
My problem is not understanding how this problem is completed it is how PPI calculates the minimum ventilation air. I opened my ASHRAE 62.1 book and found the ventilation rate for classroom (age 5-8), 10 CFM/person and 0.12 CFM. The occupant density is 25 people/ 1000 ft2. Based on this information the space will need about 463 CFM of outdoor air.
When PPI calculates the outdoor air required they only take the portion of the ventilation calc (people x CFM/person) and they do not include the second portion of the calc (area x cfm/ft2). This scares me a bit because now I do not know if I should be including this second part of the outdoor air calc when I go to take the exam.
Anyone run into this? I do not have my 6 minute solutions book on me right now, so I can't give you the problem number. It is almost at the end of the book problem 75 to 85, somewhere in there.
My problem is not understanding how this problem is completed it is how PPI calculates the minimum ventilation air. I opened my ASHRAE 62.1 book and found the ventilation rate for classroom (age 5-8), 10 CFM/person and 0.12 CFM. The occupant density is 25 people/ 1000 ft2. Based on this information the space will need about 463 CFM of outdoor air.
When PPI calculates the outdoor air required they only take the portion of the ventilation calc (people x CFM/person) and they do not include the second portion of the calc (area x cfm/ft2). This scares me a bit because now I do not know if I should be including this second part of the outdoor air calc when I go to take the exam.
Anyone run into this? I do not have my 6 minute solutions book on me right now, so I can't give you the problem number. It is almost at the end of the book problem 75 to 85, somewhere in there.