in a three phase system, phase A has phase to neutral load of 60 KW at 1pf, phase B has phase to neutral load of 72 KW at 1PF and Phase c to neutral load is 50 KW at 1 PF. To find single phase branch current
Ia=60/(480/1.732)
Ib=72/(480/1.732)=259.8 ang(-120)
Ic=50/(480/1.732)=180.4 ang(120)
Why is 120 phase displacement considered for Ib and Ic? The loads are not balanced so even if abc displacement is considered would it be 120 degrees?
Ia=60/(480/1.732)
Ib=72/(480/1.732)=259.8 ang(-120)
Ic=50/(480/1.732)=180.4 ang(120)
Why is 120 phase displacement considered for Ib and Ic? The loads are not balanced so even if abc displacement is considered would it be 120 degrees?