"I am talking about voltage phase shift with Wye connection and current phase shift with Delta connection. Not the angle between voltage and current.
If you compare Vline with V phase in star than V line is sqrt3 times Vphase and is 30 degrees ahead of Vphase. ( Drwa the vectors to find pout) and in Delta, Line currents lag 30deg to phase currents and are sqrt3 times phase currents. However when we are given KVA or VA with an angle, the angle is between phase V & I and not between Line V & I. However you can solve it without thinking about the angle."
I agree.
"For Wye connection, V (line-line)
VOLTAGE = V (line-neutral) * sqrt(3) angle 30 deg. I (line-line)
VOLT AMP =
CURRENT I (line-neutral).
Something wrong here equating Volatage with VA with current??/
For Delta connection, I (line-line) = I (line-neutral) * sqrt(3) angle - 30 deg. V (line-line) = V (line-neutral)"
The equations match your explanation.
For wye/star connection, V line is sqrt3 times Vphase and is 30 degrees ahead of Vphase -> V (line-line) VOLTAGE = V (line-neutral) * sqrt(3) angle 30 deg
For wye/star connection, line current is equal to phase current (Magnitude and angle are the same) -> I (line-line) = I (line-neutral)
For delta connection, Line currents lag 30deg to phase currents and are sqrt3 times phase currents -> I (line-line) = I (line-neutral) * sqrt(3) angle - 30 deg
For delta connection, line voltage is equal to phase voltage (Magnitude and angle are the same) -> V (line-line) = V (line-neutral)
"For this spin-up example, should we worry about the 30 deg angle?
I am not able to see the Question here but I can understand your confusion. Can you write the question here? I am sorry I should have asked you this earlier!!! "
The problem is at http://spinupexams.com/index.php?pr=Question_For_The_Week
I guess my real question is when do we do + or - 30 deg angle phase shift for voltage and current? I have understood your doubt clearly. Many have it, no worries. Now in this question the transformer does not have any meaning for calculating the current. They have given a 1-phase of load 25KVA which has a pf of .75 lagging. This lagging pf means current in this load lags the Voltage across this load by a angle 41.4 degrees. So if I take the Voltage across the load as reference ( that is Phase Voltage & angle as zero), the current will have a value of 92A and the angle of the load will be -41.1 degrees. This is not the complex load you are taking in your solution nor you have to take 30 degrees into account. I hope this has made some sense.
Thanks!