A power transformer has the following test data at rated voltage:% of Nameplate kVA || Total losses (W)

0 _____________________________ 460

50 __________________________ 2370

The total transfomrer losses (W) at 100% of nameplate kVA are most nearly:

B, Poc=460W, P50%=2,370-460 = 1,910W, P100% = (4)(1,910) = 7,640W. PT = 7,640 + 460 = 8,100W.
Somebody (Flyer???) want to tell me where that equation came from / what it is? I mean is it as simple as "oh I assume that losses square" (hence the factor of 4?) or what?

Thanks

 
Last edited by a moderator:
I am giong to take a shot at it.

At % = 0 its only the core losses = 460

at 50% its core + copper losses (I^2 * R + Pcoreloss) therefore to only find out what the load is at 50% subtract 460. 2,370 - 460 = 1,910 is the copper losses at 50%

At 100% (2 * I ) ^2 * R + Pcoreloss = 4I^2 * R + Pcoreloss

I^2 * R = 1,910

At 100% , 4 * 1910 + 460 = 8,100W

So yes you were right about the square.

 