I'm running through some problems and I think I'm using note 2 on the AC resistance and reactance chart incorrectly (pg. 768 of NEC 2014)
My previous method which appears to be wrong, is when I receive a voltage drop question that has a pf other than .85, after finding my resistance and reactance values (and adjusting for distances and/or x2 for single phase) that I would use the equation in note 2 to calculate the effective Z, then multiply by current to get the drop.
In complex imaginary questions (question 12, test 2 is an example) they do not use the Zeq equation in note 2 of the NEC and multiply the current with its phase angle to the R and X values determined from the table to get the answer.
However, in other questions (question 10, test 2) they use Vdrop = I { RL cos (theta) + XL sin (theta)}. If I were to use I with phase angle here and multiply by RL + XL I get a different answer.
I'm sure I'm missing something simple that someone can help me out with. Is it as simple as if I am given a current with a phase angle I should skip the Note 2 equation altogether?
View attachment 9357
View attachment 9358
Now that we've got all that behind us...
-------
In my opinion, neither of the provided methods are correct. Notice I said "method," and not "solution." Here's why:
In Problem 1 (the first picture above), they provide the current vector and the impedance vector and do not appear to word the problem statement in a way that references the NEC in any way; therefore, I would solve that problem using the current and impedance vectors given and would not bother to crack open the NEC and see what the approximation procedure is:
Z = [2*(220/1000)]*(0.78 + j0.052) = (0.343 + j0.023)
Vd = I * Z
Vd = (40<-10) * (0.343 + j0.023), or
Vd = (40<-10) * (0.344<3.81) =
13.76<-6.19 V
Vd% = (13.76V/120V)*100 =
11.5% <-- Sidebar: This would be an extremely undersized conductor for a feeder application, per the NEC recommendation for feeder voltage drops, but more especially for branch circuit voltage drops, which the NEC recommends should be less than 2%.
NOTE: The exact solution yielded an answer of 11.5%, while their "NEC approximated solution" yielded an answer of 11.0%. I don't know what choices you had to choose from, but hopefully you didn't have both 11.0% and 11.5% to choose from. If both choices were available, I would choose 11.5%, not 11.0% and conclude that the author of the question used the wrong method (it does happen, you know).
-----------
In problem 2 (the second picture above), the solution provided implies to me that the problem
was worded in such a way that they WANT you to use Table 9 of the NEC to solve the problem (I didn't see the problem statement, so I'm making an assumption here). If this is the case, I would use Table 9 in conjunction with Note 2 to approximate the effective impedance to find the voltage drop (Note: since I don't see the original problem statement, I'm assuming that this is a 3PH system based on the voltage magnitude provided):
Ze = (500/1000) * [(0.038*0.75) + (0.040*sin(arccos(0.75)))]
Ze = 1/2*(0.0285 + 0.0265)
Ze = 0.0275 Ohms
Vd = 230A * 0.0275 =
6.24V
Vd% = (6.24/600)*100 =
1.04% <-- Sidebar: this 350-kcmil feeder would be an acceptable size for this application.
Vload = 600V - 6.24 =
593.76V
A couple of things to note here: 1. The exact solution method that the author used is almost exactly what the NEC approximated it should be, and 2. Notice that the problem only provided the magnitude of the current, and not the current vector.
Conclusion:
For the purposes of taking the Power PE Exam test, I would read the problem and use the method they asked for (explicitly or implicitly) and choose my best answer based on that calculation method. When the problem is worded in such a way as to "force you to use Table 9" for a solution, they are likely testing your ability to use the table correctly (meaning, did you choose the correct Resistance or Reactance based on the size and type of the conductor and the conduit used?).
I don't know what NCEES has in mind for "Table 9" questions, but if I was the one writing the test question, I would set it up and I would calculate four solutions that I would give you to choose from. The four solutions would include a "near" correct answer, of course, and the other three would be based on accidentally swapping Resistance and Reactance values, choosing the wrong conduit type (maybe), choosing the wrong conductor size (maybe), using the 0.85 PF values when the problem is set up for something other than 0.85 PF...these kinds of things.