This is a thread to ask NEC code related questions.
Example16: What is the ampacityto size the feeder conductor if it supplies the following two motors?
1.One 7.5-hp, 230V, single-phase motor
2.One 5-hp, 230V, single-phase motor
Ans: Table 430.248 gives 40 A and 28 A as individual FLC of the two motors. Per Article 430.24, the feeder must be sized to 40x125%+28 = 78 A.
Size the conductor for 75 C terminals: Ans. 4 AWG (85A)
I would think the feeder conductor should be sized for 60C since it is less than 100 amps and motor design codes are not given. Can someone verify?
Example16: What is the ampacityto size the feeder conductor if it supplies the following two motors?
1.One 7.5-hp, 230V, single-phase motor
2.One 5-hp, 230V, single-phase motor
Ans: Table 430.248 gives 40 A and 28 A as individual FLC of the two motors. Per Article 430.24, the feeder must be sized to 40x125%+28 = 78 A.
Size the conductor for 75 C terminals: Ans. 4 AWG (85A)
I would think the feeder conductor should be sized for 60C since it is less than 100 amps and motor design codes are not given. Can someone verify?