NCEES Sample problem ?

Professional Engineer & PE Exam Forum

Help Support Professional Engineer & PE Exam Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

kduff70

Well-known member
Joined
Mar 31, 2014
Messages
141
Reaction score
11
Location
New Jersey
[SIZE=10pt]Good Afternoon[/SIZE]

[SIZE=10pt]I’ve attach this practices problem (118) from NCEES book but I’m stuck on why the current coming from the generator is 760 instead of 1320 amps shouldn’t the current on the delta side of the transformer increase by sqrt of 3?[/SIZE]

ncees.pdf

 

Attachments

  • ncees.pdf
    32 KB
This is actually a give me free points problem.

After you study and work transformer problems for several months, the answer will be apparent.

In this system, the current is passing thru the transformer and they are not asking for phase current in the transformer, so the current is just multiplied by the ratio of the transformer.

 
[SIZE=10.5pt]Thank you so much for your quick response that where I was a little hazy at. So I should only assume they wanted the current not unless they specify the phase current? [/SIZE]

 
I got the correct answer but in a different way than the book.

This is how I looked at this problem: generator side as primary and line side as secondary. a = 13.2/(132/root(3)) = 13.2/76.21 = 0.17321.

Know equation: Is/Ip = a; therefore Ip=Is/a = 75.93/0.17321 = 438.38A. HOWEVER, this is amperage in the phases of the delta. LINE current into the delta is root(3) larger,

Therefore Igenerator=root(3)*438.38 = 759.3A. This is close to 760 or answer (A).

 
Back
Top