I didn't see a thread regarding this question so I'll ask it.
Question:
for a 3-phase fault located at location A, the 12-kV short circuit current (amperes) is most nearly:
Distribution line length 20 miles
line impedance Z = j0.145 ohms/1000 ft
Transformer - 3ph 60/12kV, 7.5MVA with 7.5% impedance
------------------------------------
1. Why is 100 MVA used as the base power?
2. Why is the Ibase divided by the sum of the pu impedances?
Thanks in advance for any help...