The solution for this problem says that the air gap has an R-Value of 1.83.
ASHRAE fundamentals lists an air gap R-value of R-3.41 for a 3.5" air space with a 0.2 emittance that has heat flowing down (the problem says 90 deg F summer conditions, so assuming A/C inside, flow is down)
Did anyone else get hung up on this?
Also..
There is an obvious mistake in #506 where the solution uses the wrong unconditioned space temp.