For a 3-phase fault at location a, calculate the 12kv short circuit current is
Tline = j.0145/1000ft
T1 - 3-Phase, 60/12-kV, 7.5MVA Xfmr, with 7.5% impedance (inductive)
60kV
]
]________ T1 ______Tline _____ X____ to resistive load
]
]
Simple fault question
Can't figure out where I am going wrong when I choose 7.5MVA as my base.
The solution chooses 100 MVA as the Sbase.
Isc = I base * (1/Ztot)
Zbase = (sqrt(3)*12kV)^2/7.5 MVA = 57.6 ohms
Ztline = j15.321/57.6 = j.268pu
ZT1 = .075pu
Ibase = Sbase/(sqrt(3)*12kV) = 360A
Isc = 360/ (1/(.075+j.268) = 1294A
The answer should be 415A
For a 3-phase fault at location a, calculate the 12kv short circuit current is
Tline = j.0145/1000ft
T1 - 3-Phase, 60/12-kV, 7.5MVA Xfmr, with 7.5% impedance (inductive)
60kV
]
]________ T1 ______Tline _____ X____ to resistive load
]
]
Simple fault question
Can't figure out where I am going wrong when I choose 7.5MVA as my base.
The solution chooses 100 MVA as the Sbase.
Isc = I base * (1/Ztot)
Zbase = (sqrt(3)*12kV)^2/7.5 MVA = 57.6 ohms
Ztline = j15.321/57.6 = j.268pu
ZT1 = .075pu
Ibase = Sbase/(sqrt(3)*12kV) = 360A
Isc = 360/ (1/(.075+j.268) = 1294A
The answer should be 415A