I am hoping you guys can help me. Question 509 on the 2011 NCEES Practice HVAC & Refrigeration Exam seems simple, but I can't quite figure it out. Basically you have a window facing north, east and west, with Cooling Load Temperature Difference (CLTD) at 26, 55 & 72 respectively, and Solar Heat Gain Factor (SHGF) at 47, 215 & 215 respectively. Indoor temp is 75F db and outdoor temp is 95F db. U_window = 1.1 Btu/hr-ft^2-F. A_window = 40SF and A_total = 120SF. We are looking for total heat gain in Btu/hr through the windows.
I am using the MERM 13th Edition. I am using Equation 43.9 as the governing equation, which states that qdot = U*A*(CLTD_corrected) + A(SC)(SCL).
Assuming that SC=1, and SCL~SHGF, I thought the solution should be qdot = 1.1*40*(26+55+72) + (40*47+40*215+40*215) = 6732 + 19080 = 25812 Btu/hr.
It turns out I am right on the 2nd half of the equation, but wrong on the 1st half. Instead of U*A*(CLTD_corrected), they are using U*A*(T_indoor - T_outdoor). = 40*3*1.1*(95-75) + 19080 = 21270 Btu/hr.
Can someone please explain to me why they are using deltaT in lieu of CLTD? These NCEES solutions don't explain things very well!
Thank you
I am using the MERM 13th Edition. I am using Equation 43.9 as the governing equation, which states that qdot = U*A*(CLTD_corrected) + A(SC)(SCL).
Assuming that SC=1, and SCL~SHGF, I thought the solution should be qdot = 1.1*40*(26+55+72) + (40*47+40*215+40*215) = 6732 + 19080 = 25812 Btu/hr.
It turns out I am right on the 2nd half of the equation, but wrong on the 1st half. Instead of U*A*(CLTD_corrected), they are using U*A*(T_indoor - T_outdoor). = 40*3*1.1*(95-75) + 19080 = 21270 Btu/hr.
Can someone please explain to me why they are using deltaT in lieu of CLTD? These NCEES solutions don't explain things very well!
Thank you