Anyone who is using the following reference, "2015 Design of Reinforced Masonry Structures" (Concrete Masonry Association of California and Nevada), I have a question for you:
Page 146, 2nd column, has the final steps of example 4.4.3, (Min & Max reinforcement in a concrete masonry shear wall) -- My question is this, the problem statement goes out of its way to state it is SDC D, which automatically puts in you special reinforced masonry shear wall category (SRMSW). The problem concludes that 2-#4's @ 24" are required for horizontal shear reinforcement, ok fine. And it goes on to discuss the final checks for the overall steel reinf. ratios, and the one check that reads as follows is where my question is:
"For the sum of the horizontal and vertical reinforcement: 0.0014 + 0.0047 < 0.002, therefore ok …"
My issue isn't where those numbers came from , its the fact that the check is only considering a total of 2 #4 bars, and for a wall of this height (14'-0"), and given the SRMSW requirements for horizontal steel at no more than 48" OC, then there would need to be at least a couple more rows of bars to complete the reinforcement requirement. However, the check, the 0.0014 number only accounts for two total bars for all the horizonal steel, while the 0.0047 accounts for ALL OF THE VERTICAL steel as one would expect. So my issue is this:
Are they not complying with the SRMSW min. steel detailing requirements? If not, that is ok, it would just be nice if that problem stated as such, or is it because its an example problem, and not necessarily germane to the example to provide all the detailing that they didn't -- which doesn't make sense as those numbers are required for the final steel ratio checks.
Do anyone have any thoughts on this?
Thanks,
TG.
Page 146, 2nd column, has the final steps of example 4.4.3, (Min & Max reinforcement in a concrete masonry shear wall) -- My question is this, the problem statement goes out of its way to state it is SDC D, which automatically puts in you special reinforced masonry shear wall category (SRMSW). The problem concludes that 2-#4's @ 24" are required for horizontal shear reinforcement, ok fine. And it goes on to discuss the final checks for the overall steel reinf. ratios, and the one check that reads as follows is where my question is:
"For the sum of the horizontal and vertical reinforcement: 0.0014 + 0.0047 < 0.002, therefore ok …"
My issue isn't where those numbers came from , its the fact that the check is only considering a total of 2 #4 bars, and for a wall of this height (14'-0"), and given the SRMSW requirements for horizontal steel at no more than 48" OC, then there would need to be at least a couple more rows of bars to complete the reinforcement requirement. However, the check, the 0.0014 number only accounts for two total bars for all the horizonal steel, while the 0.0047 accounts for ALL OF THE VERTICAL steel as one would expect. So my issue is this:
Are they not complying with the SRMSW min. steel detailing requirements? If not, that is ok, it would just be nice if that problem stated as such, or is it because its an example problem, and not necessarily germane to the example to provide all the detailing that they didn't -- which doesn't make sense as those numbers are required for the final steel ratio checks.
Do anyone have any thoughts on this?
Thanks,
TG.