The answer is D.Not sure where an actual answer is in a book, but logically it is correct. When you size the overcurrent protection, you have to size the conductors to meet your load. The insulation has a temperature rating that determines how many amps the conductor is rated for. The overcurrent protection has to be sized so that if the ampacity is greater than the load it is sized to handle, the circuit breaker will trip and protect the insulation of the conductor. For thermal/magnetic circuit breakers, the magnetic portion protects against faults and the thermal portion protects against overloads; both to protect the conductors insulation.
Is answer A correct? Yes, but preventing fires comes from protecting the insulation. B, It does isolate the circuit, but only to save the insulation of the conductors. C, It can protect the device, but ground fault protection is what really protects devices.
This is one of those cases of what is “most” correct.
I do not have code in front of me right now but I believe it's section 240 something that talks about overcurrent protection.I can't find this in NEC or any other literature I was looking in. I could see this being a PE question, but I don't want to take this books "word for it" without verifying it.
View attachment 19640View attachment 19639
Correct. The other answers are somewhat correct, but D is most correct. That is what I elaborated on in the first paragraph.The answer is D.