Kaplan Afternoon #40

Professional Engineer & PE Exam Forum

Help Support Professional Engineer & PE Exam Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

cabbagekid2

Member
Joined
Oct 18, 2010
Messages
21
Reaction score
0
Location
Hawaii
Hello, another NEC Kaplan question...

The problem is asking for the full load current of the motor. Here are the specs: 3 phase, 100HP, 460V, 0.8 pf lagging, synchronous motor with normal torque characteristics.

Looking at 2008 NEC Table 430.250 I found 101A as the full load current listed. However, in the answer for this problem they multiply 101A by 125%. I know you are suppose to do this when sizing conductors for motors, but isn't 101A the Full Load current? And then 125% is just to size the conductor and not the Full load current?

Gah...only two more days!

Thanks!

 