It's a 12KV fault 20 miles down line from the substation transformer. Distribution line has a Z of j.145 ohms per 1000'. Sub transformer is 7.5MVA with 7.5% impedance. Wants to know the fault current.
After looking in the back of the book, I'm confused. Did they arbitrarily pick 100 MVA as their S base, or was it because 7.5M /.075 is 100M?
When they calculated the transformer impedance they said...
.075 pu x (100MVA/7.5MVA) = 1.0 pu
I know where .075 pu came from, but what is 100MVA/7.5MVA? I should know this but I haven't done pu in a long time. TIA
After looking in the back of the book, I'm confused. Did they arbitrarily pick 100 MVA as their S base, or was it because 7.5M /.075 is 100M?
When they calculated the transformer impedance they said...
.075 pu x (100MVA/7.5MVA) = 1.0 pu
I know where .075 pu came from, but what is 100MVA/7.5MVA? I should know this but I haven't done pu in a long time. TIA